  1. Do I need to have a GFCI for an electric 4 wire range?
  2. When I replaced the current 2-pole 40 amp circuit breaker with a 2-Pole 40 amp GFCI replacement for electric range the circuit trips and does not turn on. I have confirmed that it's wired correctly and have not been able to figure out why it's tripping. The ground and neutral are connected properly.
    The range is 4 wire.

This one is resolved!
Had to cut the "jumper" between ground and neutral.
Had to cut the "jumper" between ground and neutral.

Best Answer

Look at the wiring on the connection block on the back of the range. Make sure that the neutral and the ground are not connected. If the neutral and ground are connected, the GFCI will trip.

The neutral and ground are not supposed to be connected on the connection block with a four wire cord and ground going all the way to the panel. Some installers aren't properly trained and will leave the neutral and ground connected on the back of the range.