Before you begin, make sure to pull out/turn off the serviceman switch, and/or turn off the breaker, to remove power to the unit. Once you open the unit, you'll want to discharge the capacitor(s). A charged capacitor can store enough energy to kill you, so you want to make sure you discharge them.
Test the motor
To check the motor, you're going to want to check the resistance of the coils in the motor. To do this, you'll need a multimeter set to measure resistance in Ohms. You'll also have to identify the wires, which will depend on the unit you're working on. Use the schematic printed inside the unit, or in the manufacturer's documentation, to determine which wires are which. You'll want to determine which wires connect to the Common, Run, and Start motor terminals.
Once you know which wires go where, you'll measure the resistance as follows:
- Common -> Start
- Common -> Run
- Start -> Run
If you sum the value measured between Common and Run, with the value measured between Common and Start. You should end up with a value right around what you measured between Start and Run. If the values are way off, the motor is bad. If any of the readings are infinity (open), it means the coil is broken and the motor is bad.
NOTES:
- Depending on the motor, there may be multiple speeds. If so, you'll have to measure them as well, to determine if those coils are good.
Test the capacitor
When checking the capacitor, the first thing to do is a visual inspection. If the capacitor is bulging, or has released the magic goo. Then the capacitor is bad, and needs to be replaced.
Make note of all the wires connected to the capacitor, then disconnect them. Then set your meter to measure capacitance in microfarads (uF). Touch one meter lead to the terminal marked C
(common), and the other to the terminal marked FAN
. Hold the leads on the terminals until the meter settles, then take note of the reading. With one lead still on C
, put the other lead on HERM
. Again, wait for the meter to settle, and note the reading.
Compare the readings you took, to the values printed on the side of the capacitor. The measured values should be within the tolerances printed on the capacitor, otherwise the capacitor needs to be replaced.
Fixed! Turned out, it was an issue with the condensate drain line.
I had moved it and it had become just ever so slightly raised, so that the line had become double trapped. The collector was filling up with water, and tripping the secondary pressure switch.
The reason I wasn't getting a code, was because the water was gurgling, or bubbling, as the negative pressure pulled the water back up the condensate line. This caused the pressure switch to fluctuate rapidly, which is also what caused the sputtering flame problem. This rapid fluctuation, which was picked up by a multimeter, was too fast for the control board to actually register a fault.
Fixed the condensate line, and all is well.
Haven't been able to explain the cover on/cover off phenomenon, may have simply been coincidence. It ran all night, all buttoned up, without issue.
Best Answer
For posterity - replacing the cap seems to have resolved the issue.