My bathroom, inside near door, has a 2-gang box, containing 2 light switches, powering combination ceiling light and fan. This box is fed by hallway lighting circuit, and the work box is not covered by GFCI.

The changes I want to make are:

  • Exchange both switches with a "2 horizontal switch" device, freeing up a gang (example: Leviton 5634-W)
  • Install a USB-ONLY outlet (example: Leviton USB4P)

My question is whether this change is "to code" (NEC)? I am in Northeast USA (NH).

For completeness: My bathroom electrical outlets ARE on a different circuit, in a different work box, and yes that is protected by GFCI.

The question is about adding a USB "outlet" to an area that normally requires all outlets to be GFI. My understanding is what I plan would be OK because these are low-voltage.

Best Answer

No, Class 2 power outlets (such as USB receptacles) are not required to have GFCI protection

This can be drawn from the fact that the GFCI requirements in NEC 210.8(A) are specifically restricted to 125V, 15 and 20A receptacles:

(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(A)(1) through (10) shall have ground-fault circuit-interrupter protection for personnel.

(1) Bathrooms

and is further justified by the definition of Class 2 circuit in 725.2 already taking shock hazards into account:

Class 2 Circuit. The portion of the wiring system between the load side of a Class 2 power source and the connected equip‐ ment. Due to its power limitations, a Class 2 circuit considers safety from a fire initiation standpoint and provides acceptable protection from electric shock.

(See also the fact that 210.8 is not referenced in NEC 725.3.)