Are GFCI outlets allowed on new circuit installations

gfcinec

A comment thread on GFCI outlet on 2-wire ungrounded question led to a discussion of whether GFCI is better/worse or even permitted at point-of-use (GFCI/receptacle) instead of GFCI/breakers in the panel:

But regardless of how much people sing the praises of "point of use reset" in GFCI it's still going the way of the dodo bird since code is now requiring the panels GFCI.

and later:

It is simply no longer code for new installs for a reason, the NEC is not stupid. I've tried explaining why if you don't want to accept it that's fine but it is where things are headed no matter what you want. Sorry.

Presumably this is a non-issue for any existing installations as many panels are perfectly, legally, functional, but incapable of adding GFCI breakers due to technical limitations or simply because there are no listed GFCI breakers available.

Can the code experts please clarify whether or not, in new work with a modern, GFCI-capable, panel, GFCI/receptacles are permitted instead of GFCI/breakers? Reference to any such change in NEC 2017, NEC 2020, any officially proposed changes or specific jurisdiction code modifications are appreciated.

Best Answer

The Code doesn't specify location of protection.

NEC 2017

210.8 Ground-Fault Circuit-Interrupter Protection for Personnel. Ground-fault circuit-interrupter protection for personnel shall be provided as required in 210.8(A) through (E). The ground-fault circuit interrupter shall be installed in a readily accessible location.

Th 2020 Code changes (E) to (F), and reorganizes paragraphs.

The biggest issue is interpretation of "readily accessible".(e.g. Is the receptacle behind the fridge or microwave readily accessible?)