Basement Sub-panel Breaker Size

subpanel

I am confused about small-appliance branch circuit for service load calculation. I am trying to size my breaker for a sub-panel in my basement from my main 200A panel.

I will have a main room, wet bar area, bedroom, and bathroom.

I have calculated the following loads:

  • Lighting Wattage = 790sq ft x 3 = 2,370 VA
  • Under counter 46 Bottle Wine Cooler: 90VA
  • Under counter refrigerator: 240VA
  • HVAC Heat Pump = 4,320 VA
  • HVAC Air Handler = 960 VA
  • HVAC Heat Strips = 4,800 VA
  • Sump Pump = 1,200 VA

Do I need to consider any small-appliance branch circuits in my calculation?

Best Answer

The small appliance requirement is for the kitchen counters 2 as 20 amp circuits. If you want you can add a circuit for the bar but it would not be required.