Bond CSST to Water Pipe – Allowed in 2017 NEC 250.104(B)

coppercsstgasgrounding-and-bondingpipe

I am looking to bond out CSST gas line which is in our crawl space of the house (dirt floor) and the copper water pipe is close by. I was wondering if CSST can be bonded to the copper water pipe in Arkansas. I read through the 2017 NEC, specifically focusing on 250.104; however, I could not figure out a clear answer. I know that in some states, you are allowed to bond to the water system but I am specifically looking for Arkansas. Arkansas adopted the 2017 NEC with amendments on 1 Jan 18. Thank you.

Best Answer

The gas system only needs to be bonded at one point

Bonding the black iron at the meter to a legal bonding point (anywhere on the grounding electrode system, basically, using a listed tap connector such as an ILSCO GTT-2-2 to connect the gas bond wire to the GEC, or simply by landing the gas bond wire on the intersystem bonding termination device if one is present) will suffice for bonding the entire gas system; there is no need for an extra bond point for the CSST if the system is already bonded, as per this tech bulletin.