Can a 120v pool timer be used on a two-wire 240v circuit

240v

I am replacing an Intermatic mechanical T104 single circuit timer with a new Intermatic P1353ME unit that can control 3 individual equipment items in addition to the timer clock.

Each of the three circuits can control either 120v or 240v equipment items independent of the timer power source. Can this timer be used with existing 240V, 20 amp, 2 wire plus ground power feed from the panel?

I plan to use this 20 amp circuit to power three equipment items at 240v. Total load is below the 80% load for the 20 amp circuit.

With an existing 2 wire dedicated 240v circuit, what leg is considered "Line" and what leg is considered "Load"?

Best Answer

This timer can be hooked up to your 220V, 20 AMP, 2 wire plus ground circuit from the panel. Since you don't have a neutral you won't be able to ever run any 120V equipment unless you change your wiring. This timer have the ability to switch both hots on a single 220V load but not on three separate equipment items. You'll only be able to switch one hot on each piece of equipment. The other hot will always be connected to a load wire.

With your 220V circuit, the two hot legs from the panel will be your line 1 and line 2. Your wires from your three pieces of equipment will be your load 1 and load 2 for each piece.