Concrete – Distance between edge of concrete for anchor bolts

anchorconcrete

In residential construction, placing anchor (j bolts) for the sill plate, I have always read that it's best to stay towards the outside edge of the foundation and face the J portion towards the interior of the home. For an 8" thick concrete wall, I have always used ~3" in from the edge. This allowed a 2×6 plate to have the anchor be about 1/4" off center of the board.

Wondering how you guys do it, and if there is a better way. I always try to get the concrete guys to provide 10" instead of 8" bolts, and they are typically 5/8" diameter.

Also – Do you actually preset the anchor bolts in blocks of wood or rebar cages, so that the hook part of the J slips under the top horizontal rebar?

Best Answer

The Code requires an edge distance based on the size of the bolt:

1) 1/4” = 1 1/2”

2) 1/2” = 2 1/2”

3) 5/8” = 3”

This is based on standard grade concrete, (i.e.: 2500, 3000, etc.) If you use a “high-strength” concrete it can be reduced. (See ICC Chapter 19, Table 1908.2)

Generally, I see “J-bolts” installed after the foundation wall is poured. This is primarily because we want a smooth surface for the sole plate to rest on. The bolts can be wiggled into the concrete and twisted so it hooks under the top horizontal rebar, which should be approximately 3” clear down from the top of the wall.

Yes, 10” anchor bolts are now required with 3” square washers in any high-wind or seismic area.