Condenser fan and compressor don’t start, electrical looks good though

air-conditioningcompressorrelay

After replacing the fan, starting capacitor, and running capacitor, the system ran normally for ~1 day. Now nothing is starting.

I got a fieldpiece multimeter and tested all of new capacitors, connections, motor ohms, continuity, and current. All measurements look good, but current isn't flowing more than 0.05a, and capacitors don't seem to be charging.

There is 240v going to it, not sure what else to attempt, any suggestions are welcome.

Goodman gx160481fa

Best Answer

My advice would be that you should have called an HVAC company first since this is what they are "schooled" in. I have to ask, why did you replace the fan and compressor capacitors? Were they bad or were you just guessing on a repair effort. When you say 240 is going to it, what do you mean? Where are you measuring the 240 volts. Is it at the incoming power supply or at the starter/contactor going to the compressor? Is the contactor energizing? Do you have 24 volts at the coil of the contactor? Is the fan running in the indoor air handler? The problem could be a tripped circuit breaker or blown fuse (now showing my age),at the 24 volt power source. Please call someone familiar with A/C service before you do something you can"t fix. These units can hurt you. Hope this helps.