I have two old thermostats (one for heating, the other for cooling) that I would like to replace with a single Nest E unit. I have central air and gas heating.
Cooling thermostat has the following connections:
R (Rh and Rc are jumped) G and Y
Heating thermostat has these connections:
R (Rh and Rc are jumped) and W
Combining these two into a single unit like Nest E seems simple – Nest has G W Y and R connections, HOWEVER – there is only a single R connection and from these two thermostats I have two R wires.
My question is 1) Do I have two transformers and therefore I need a unit that can support two transformers with separate Rh and Rc connections? Is there any way for me to check if my HVAC system is running from a single or two transformers? 2) If I do have a single transformer (again, how to confirm this) – can I connect just one of the two red wires and cap the other one off?
Thanks for any advice!
Best Answer
If you have forced air A/C and radiant heat, you almost certainly have two separate transformers. So you'll have to use a thermostat that can work with separate transformers.
If the thermostat you choose requires a
C
wire, you'll likely want to supply theC
from the A/C transformer. It's almost always easier to get theC
wire from a forced air system, than from a boiler. Also, some thermostats actually require that theC
wire come from the cooling system.Once you've selected the thermostat you want, connect the wires as follows:
Rc
andRh
.R
from the A/C toRc
.Y
from the A/C toY
.G
from the A/C toG
.C
from the A/C toC
. (Where required)R
from the boiler toRh
.W
from the boiler toW
.Extra reading
With two separate transformers, the wiring should look something like this.
Notice there's no jumper between
Rh
andRc
.The green line represents the equipment grounding in the building.
In this situation, everything works as expected.
If you have two separate transformers, but only connect one of the
R
wires. You could still have a complete circuit, if the transformers secondaries are bonded. However, since you're using the buildings grounding system to complete the circuit, you may find that there's not enough power to get things to work properly. You might find that the A/C works fine, but the heat doesn't (or vise versa, depending on how it's wired).Two separate transformers, with only one supplying the thermostat.
Notice there's a jumper between
Rh
andRc
.If you have one transformer that is supplying two
R
wires. It's the same as having one transformer, and using a jumper to connectRh
andRc
. It's just a really long jumper.If you have two transformers, and you connect a jumper between
Rh
andRc
. You'd be connecting the transformers in parallel. If the transformers are identical (or close enough), this may not be a problem. As long as the transformers are in phase (and identical), everything should be at the same voltage potential. If the transformers are not in phase (or not identical), you'd be creating a short-circuit.If you have two
R
wires at the thermostat. The best bet is to remove the jumper betweenRh
andRc
, and connect the separate wires to separateR
terminals.