I am installing 120v wiring for a dorm-type setting, and some of the rooms are over 70 feet from the breaker panel. The NEC says that the home run may not exceed 50 feet for 14 AWG and 70 feet for 12 AWG conductors. If it does the first receptacle in the branch circuit has to be an AFCI receptacle.
So, in the case where the 1st receptacle is more than 70 feet from the panel do I need both (an AFCI breaker and an ACFI Receptacle)?
Best Answer
I could be wrong here, but the way the code is written, the circuit length should only matter if...
210.12(A)(1) allows the circuit to be protected by a "combination-type arc-fault circuit interrupter", without any mention of the length of the circuit. So I would expect as long as you're installing a combination-type AFCI, and not a "supplemental arc protection circuit breaker". Then there should be no problem. But I've been known to misinterpret code from time to time.