Do I need to run electrical wires exiting the breaker box on the exterior wall of the house & traveling across the wall in conduit or can the wires be stapled to the wood siding with steel staples?
Does electrical wires on exterior need to be in conduit
conduit
Related Topic
- Electrical – proper way to run conduit on top of siding
- Electrical – EMT or PVC Conduit For Exterior Above Ground Electrical Run
- Electrical – Outdoor box or conduit body
- Electrical – Is this plan for running a circuit in buried conduit correct
- Wiring – What are the options for getting this mess of cables under control
- Electrical – Does MC cable need protection in an exterior wall penetration
Best Answer
In the US -- the general rule is that outdoor rated cables (MC, SE, and sunlight-resistant UF are the only ones you'll see in residential work -- AC isn't allowed in damp/wet locations, nor is NM of course) can be run in the open provided they cannot be subject to physical damage -- if your cable is running anywhere where people can run into it, mow it, whack it, or trip on it, you'll need to install your wire (THWN) or cable (there are no Code objections to pulling intact SE or UF through conduit, although it may annoy the next electrician who works on it) in RMC, IMC, schedule 80 PVC, or RTRC-XW to provide protection from said physical damage, as per NEC 300.5(D)(4):