Electrical – 100 amp sub-panel replacing old fuse box

electrical

enter image description here

I have this old fuse box in the attic (pictured, basically acting as a junction box) and 6 wires total running into it, 4 are knob and tube, so two are hot, two neutral, they all go dead when one 15 A breaker is tripped in the basement, and the other two wires are more Romex-like wires with hot, neutral, ground all bundled together, they are run on a 15A breaker and a 20A breaker in the basement. I wanna connect the knob and tubes to the Arc-fault breaker I got in the new square D sub-panel which will go in he attic, the knob and tube aren't in the basement for me to put the arc fault breaker in down there and connect to them

Best Answer

I agree with Harper and RME. You do not need a sub-panel.

A junction box will work just fine especially in an attic even if it is a walk-in attic.

The National Electrical Code requires, with few exceptions, that a conductor be protected at the point where it receives its supply.

The fact that you can shut all of this off with three breakers in the basement means that they are already protected.

If you wish to add AFCI protection then just replace the breaker or breakers in question with an AFCI breaker. Much easier and cheaper.

Good luck and stay safe!