Electrical – 12/3 cable coming from box, is this correct

electricaljunction-boxrewirewiring

I have the following junction box:
enter image description here

The cable coming from the left is from the fuse box, it's 12/3 (aluminum). The cable going straight down is going to a switch (it's 12/2, aluminum). The other cable going down and curving slightly to the right is going to a light fixture (14/2 copper). The cable going up is also going to a light fixture (14/2 copper). The cable going to the right is carrying power to another room (12/2 aluminum).

So there's essentially one X/3 coming in, and four X/2 going out. The aluminum to copper needs to be property pigtailed with a purple wire nut (which is accepted here). Let's ignore that issue for now; I'm trying to understand if my assumptions about this setup are correct and why it might have been set up this way.

Here is a drawing I made of the wiring (I omitted the other lights, as they are just pigtailed together):
enter image description here
(B = black wire, W = white wire, R = red wire)

When I open the switch, the lights turn off, as expected, and voltage drops to 0 on the red wire (R) coming from the fuse box. The black wire going to the other room remains live.

When I close the switch, the lights turn back on, and there is now 120 volts on the red wire (R) going to the fuse box. The wires going to the other room remain live, of course.

Now, I'm assuming that the 12/3 cable is the one delivering power to this circuit, and is coming from the fuse box. The white wire is shared common for the lights and the other room. Which makes it seem like the red wire is useless. Does this seem correct?


To me, it seems the 14/2 wires were retrofitted into this box to add additional lights, and originally this junction box was the one that had a light attached to it. Which makes me think that the red wire from the fuse box should be used as the neutral/return for the lights; so the lights and the other room both share power from the same black from the 12/3, but return power on the other two wires, separate from each other.


UPDATE: After reading the comments and answer and looking around a bit more, it seems the 12/3 cable probably terminates in this junction box (and the red cable isn't attached to a load):
enter image description here

Best Answer

Red is carrying switched-hot off to another location where a light might have been fed from. It's not going straight back to the panel. If you follow it you'll probably come to a good place to fork off more light fixtures.

Red is the preferred color for switched-hot.

Now there are a few issues with this box. It's extremely over-full. You have 11 wires in there + ground + cable clamps, so I see 13 wire counts... at #12 that's 29.25 cubic inches required for that box. Those octagon boxes are about half that, so you'll need to get an octagon "extension box" to put on top of this box. Or you could change the box to a 4-11/16" square box (42 cubic inches).

As far as the aluminum to copper splices, purple wire-nuts may be Code but they sure like to start fires. You'd be wise to consider Alumiconns for up to 3 wire connections, and MAC Block connectors for 4+ wires. The MAC Block has 2 voids and allows up to 4 wires per void (though the 4 must be the same metal).