I have a 120v 20a receptacle that is measuring 220V at the outlet:

enter image description here

In the panel this circuit is controlled by a double pole 30amp breaker:

Breaker

I was using a 120V window AC unit in this outlet and it was working fine for years. How is this possible? The unit recently started having problems and I was looking to replace it with a 220V unit. Can I do that with the current configuration? What else do I need to consider (wire gauge and amperage needs of the new unit come to mind)?

Here is the wiring of the receptacle:

enter image description here

Edit:
Here is the cord the cord on the unit I'm replacing it with showing it as 25amp.

And this is a link to the replacement unit in question

Best Answer

As you've noticed, someone has wired this 20A 120V receptacle for 240V at 30A. That is very dangerous, and it's quite lucky your house never burned down. Most likely your old AC was designed to accept either 120 or 240V, and so it didn't notice the difference.

Based on your pictures of the current wiring, I believe you have 10 gauge wires (wire looks like orange sheathed NM) which can handle the 30A it's breakered for. It would be wise to double-check this with a wire gauge before upgrading to a larger air conditioner though.

To replace the current unit with one that requires 30A of 240V, assuming you already have 10 gauge wire in the wall, you'll only need to change the receptacle to the correct one, such as a NEMA 6-30. Or, if your new AC wants 20A of 240V, use a NEMA 6-20, and also change the breaker to a 20A one.