If you run a 20 amp circuit (12/2) with shared lights AND receptacles, can you use a 15amp switches? Its my understanding that the switch is rated for the load its carrying (lights), but what about the load of the whole circuit? Lets say you have a room on one 20 amp circuit supplying outlets(15amp rec) and lights(15amp switch)you plug in a vacuum cleaner, have mini fridge running, and a fan plus lights, you pull more than 15 amps on the circuit. The breaker won't flip, but will the light switches rated for 15amp be ok?
Electrical – 15amp switch load clarification
electricalwiring
Related Topic
- Wiring – Fridge and freezer on 15amp circuit break via 14-2 wiring
- Wiring – Kitchen Wiring 14 to 12 Neutral
- Electrical – Using a 15 Amp Switch on 20 Amp Circuit
- Wiring timer switch into 2-gang switch setup with common load (red) with downstream load
- Electrical – 20 amp Circuit, 15 amp switch that controls receptacles ok
- Electrical – size sub panel needed for mini house
- Electrical – Is it ok to run 14 gauge wire for lighting off of a chain of 12 gauge outlets on a 20 amp breaker
Best Answer
Using 15A light switches to switch <15A on a 20A branch circuit is OK, unless you're switching receptacles!
As it turns out, NEC 404.14(A) permits the use of a snap switch (general light switch) to control any hardwired, non-motor load up to its rating, or motor loads under specific conditions (informational notes omitted):
Note, though, this doesn't hold true when you're switching receptacles, as someone could plug say, a space heater into the receptacle(s) and exceed the rating of the switch as a result (informational note omitted again):
The reason why is in your hypothetical case, the wall switches are not in the path of the current the vacuum draws, basically. (Keep in mind that current flows in loops and that loads connected are in parallel.)