Can I have an exterior 200A meter and disconnect with the 200A main panel in the interior some 20-30 ft. away? It has to meet California residential code.

I'm trying to avoid the cost of an exterior main panel in addition to a 200A interior sub-panel.

If so, what products should I look for for the exterior? I was thinking "meter socket with disconnect" but I can only find exterior panels.

Here is an elevation plan:
enter image description here

I currently have a 100A exterior panel at the meter which I need to upgrade to 200A but my contractor recommends having a panel in the interior hallway for convenience.

I can't add the panel close to the meter in the interior because of house configuration. It will have to be 20-30ft away.

Thanks.

Best Answer

I believe the Google words you are looking for are meter main or meter main combination.

As long as the wiring in your house is downstream of a main breaker (not merely disconnect), that is fine. Remember since all the power from your service runs through it, you get to apply the 310.15(B)(7) derate of 83%; your wire only needs to be rated for 166A, not 200A.