Electrical – 3 wire sub to main panel upgrade

electrical-panelwiring

I have a subpanel in a detached garage that has 3 wires run from the main panel. To the main there is 400 amps run from the electric provider with 3 wires, and it is split to have 200 amp service to the garage with 3 wires. I know code now says it should be 4 wires, but what can I do to add safety to this service short of digging up concrete and dirt and adding that 4th wire?

Best Answer

When the building was built code was probably 3 wire ( this was the standard for decades). What you have was quite common until the1999 NEC code change. A 200 amp feed would normally be in conduit and if metallic that could be used to meet today’s code. If it is a direct buried feeder and you feel the need to update it a separate ground wire is now allowed, in most cases a panel that was 3 wires will have the neutrals and grounds connected or even on the same buss this will need to be changed to isolate the neutral from ground. Also every receptacle will require GFCI protection to bring it up to current code but this is not required as your existing configuration is grandfathered. If you really think it is unsafe add the GFCI protection.