I recently swapped out a 40 amp breaker (previously for an oven/range) to a 30 amp GFCI, on the other end will be a L6-30 receptacle (2 hots, 1 ground). My question is what to do with the neutral wire on either end of the line. In the panel, is it correct to connect both the neutral from the line and the neutral pigtail from the breaker to the neutral bar, leave the neutral terminal on the breaker empty, and then cap the neutral at the receptacle? Or should the neutral from the line be connected to the neutral terminal on the breaker?

Through some research I think I found that GFCI only needs the neutral for 120v loads, just not completely sure

Best Answer

You connect the 2 hot wires to the breaker like you would on any other double-pole breaker. You also must connect the pigtail from the breaker to the load center neutral terminals. Connect the ground wire from the circuit to the load center ground terminals. The neutral terminal on the breaker is just unused in this case.

See for example this diagram from Square D instructions:

Wiring Diagram

But certainly make sure to check the instructions included with your specific breaker. If you don't have them, I've had good luck finding instructions on the home improvement store websites - seems like they are easier to navigate than the manufacturer websites.