Electrical – 6/3 NMB in non-metallic conduit

electrical

I’m running a 50A circuit using 6/3 NMB from my interior panel to a hot tub. I’ve got the required GFCI protected disconnect within direct line of sight of the tub (about 15ft from the tub). I have 3/4” LFNMC that is planned to use once the wire penetrates to the exterior of the crawl space. My question is….is it acceptable to run this cable through the conduit if I remove the romex jacket? It would need to be in the conduit for about 8ft from the crawl space to the disconnect and then about 25ft or so to get to the connection inside the hot tub. Thanks in advance for your help!

Best Answer

Don't make your life harder than it needs to be!

First off, shucking NM of its jacket is no good, because the wires inside NM cable aren't marked properly for individual use. Second, pulling NM through outdoor conduit is unacceptable because NM is no good in wet areas due to the paper separator layer between the jacket and the wires (which wicks moisture up the cable, leading to hard-to-troubleshoot failures later), and all outdoor conduit is considered a wet location by NEC 300.9:

300.9 Raceways in Wet Locations Abovegrade. Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.10(C).

Third, there's absolutely no reason to make your life this hard: pulling 4 6AWG THHN wires through your conduit (hot, hot, neutral, ground) will be far easier than trying to jam a cable through there. So, I would simply get an appropriate amount of 6AWG THHN (black, white, green is fine) and use that instead.