Adding a 60amp sub panel (4breakers) on the 2nd floor for a dehumidification system and some misc. Running 100 feet of 6/3 wire. I am assuming that I can use the ground wire in the 6/3 from that sub panel ground bar to the main panel ground bar. This is not in a separate building so I don’t think NEC requires grounding rods.
And if so does anyone know the limitation on the length of a ground wire if indeed a separate one is required for the panel itself. Washington country Maryland.
Electrical – 60 amp sub panel, 100 ft away from main panel. Grounding rod or not
electricalelectrical-panelgrounding
Related Topic
- Electrical – Sub Panel grounding questions… wire size, how-to’s
- Electrical – Sub-panel wiring, grounding, disconnect
- Use the grounding rods of a main panel as the grounding rods for the sub panel
- Electrical – How should a sub panel be grounded if next to the main breaker
- Electrical – Campground sub panel grounding question
- Electrical sub panel grounding
- Electrical – Grounding electrical sub panel in separate structure
Best Answer
Same building, just supply ground and neutral in appropriate sizes and separate, and be sure that ground and neutral are not bonded in the sub-panel.