Electrical – 60C or 75C wiring for 60C/75C breaker & output heatsink

electrical

If you have a THHN wire rated up to 90C. You can only use either 60C or 75C for a 60C/75C breaker. What are the conditions where you could use the 75C?

I understand the temperature limit is because the internal parts circuit breaker can get this hot and it needs the conductor to dissipate the heat. But what if you install a big heatsink just outside the breaker. Then you can use 75C or even 90C already?

Best Answer

The idea of modifying the breaker so you could use smaller wire is wrong on a number of levels but I'll just discuss one.

But what if you install a big heatsink just outside the breaker. Then you can use 75C or even 90C already?

The electrical code requires that most of your electrical system be listed by a nationally recognized testing laboratory (NRTL) such as Underwriter's Laboratories (UL).

The electrical code requires that listed equipment must be utilized according to the manufacturer's instructions; not doing so violates the listing. If you modify a listed device, it's effectively no longer listed.

Adding a heat sink to a breaker would be a modification, and as such would not be permitted.