Electrical – AC: Powering a 25 amp appliance from 2×20 amp breakers

circuit breakerelectricalwire

I want to use a 25 amp appliance but only have 20 amp breakers.

Work around
I am thinking of hot wiring the output of 2×20 amp breakers so that the 25A load is distributed between 2 breakers instead of one, preventing the breakers from tripping and giving me up to 40A of power to work with.

Is this possible and would it work?

Update
Thanks for the feedback.
I decided it is best to get an electrician around to wire a new 30A breaker, wiring and new wall socket.

Best Answer

You so not want to do this. If you have a true 25A load then install the proper 30A or 40A single breaker and the proper wiring for that amperage (10AWG for 30A breaker or 8AWG for 40A breaker) in a single circuit to a listed receptacle rated for that current rating.

Here are some of the problems that you have with what you propose:

  1. There is never any guarantee that both parallel breakers will split the current equally.
  2. If one breaker goes open on a current overload the other breaker and circuit is left trying to source your 25A load through wiring that is rated for 20A or less. This can cause overheating. One would hope that in this case the second breaker would open but with just a 5A overload on a 20A breaker it may not trip right away.
  3. In the case that you are on a split phase AC mains power system (such as used in the USA where 120VAC per phase is available) you could mistakenly try to parallel up two 20A breakers that were on opposite phases. Doing so would result in a direct short across the 240VAC and could cause lots of sparks to fly.

So....again do not do the kludge that you are proposing and install the proper single breaker/wiring/receptacle to support your 25A load in a safe and reliable way.