I want to use a 25 amp appliance but only have 20 amp breakers.
Work around
I am thinking of hot wiring the output of 2×20 amp breakers so that the 25A load is distributed between 2 breakers instead of one, preventing the breakers from tripping and giving me up to 40A of power to work with.
Is this possible and would it work?
Update
Thanks for the feedback.
I decided it is best to get an electrician around to wire a new 30A breaker, wiring and new wall socket.
Best Answer
You so not want to do this. If you have a true 25A load then install the proper 30A or 40A single breaker and the proper wiring for that amperage (10AWG for 30A breaker or 8AWG for 40A breaker) in a single circuit to a listed receptacle rated for that current rating.
Here are some of the problems that you have with what you propose:
So....again do not do the kludge that you are proposing and install the proper single breaker/wiring/receptacle to support your 25A load in a safe and reliable way.