I'm having an electrician replace my 2-unit meter main Zinsco panel with a new Siemens WP2211 panel. There will be two 100A breakers for the two units in the complex. The panel lists the following acceptable breakers:
QP, QPH, HQP, HQPH, MP-T, MP-HT. The QP and MP-T have a 10 kA AIC, the QPH has 22 kA and is only about $15 more than the QP. The HQP at 65 kA is three times the price, and presumably overkill.

Given that this is a service entrance, I assume the amount of short circuit current available from the utility is pretty substantial.

Is there a recommended value for residential service entrance breakers? I'm leaning towards the 22 kA QPH.

Thanks

Christian
enter image description here

Best Answer

You'll have two services there.

As you say, according to PG&E, they design their facilities so that 10KA of short-circuit current is not possible for new single family drops. However, being a duplex with 2 meters, I could imagine them supplying twice the capacity.

That would be 20KA. Since only one service will have a problem at a time, the worst-case assumption is that each service needs to handle that independently.