Electrical – Are power outlets in a home out of phase with each other

electricalelectrical distributionelectrical-panelwiring

I'm working on a science project and there's one aspect of home wiring I need to find out (don't worry, I'm not messing with wiring – this is all on paper). Since 120V outlets in a home can be wired to either of the two 120V legs that come in from the power company, would it be a true statement that outlets on different breakers could be out of phase with each other? In other words if Bedroom 1 is tied to leg 1 and bedroom 2 is tied to leg 2 is it reasonable to assume that the sine waves measured from outlets in bedroom 1 will be out of phase with the sine waves measured from outlets in bedroom 2?

Best Answer

Sort of. It depends on your frame of reference.

If you're looking at the ungrounded (hot) conductor from each receptacle, you'll end up with a 240 volt circuit. Since it's a single circuit, it can't be out of phase with itself. If you hooked up an oscilloscope to the ungrounded (hot) conductor of each receptacle, you'd get a single 240 volt sine wave.

If you're looking at the two separate circuits (e.g. the ungrounded (hot) and grounded (neutral) conductor from each receptacle), then you'll end up with two 120 volt circuits 180° phase shifted from each other. If you hooked up the oscilloscope to the ungrounded (hot) conductor and grounded (neutral) conductors from each receptacle (4 leads instead of 2), you'd see two 120 volt sine waves 180° phase shifted from each other.

The two sine waves should look something like this.

sine waves from single split phase transformer

Because the waves are phase shifted 180°, the electrical potential between the legs (at the peak) will be 240 volts. While the potential between either line and "neutral", will be 120 volts.

If the waves were not phase shifted, they'd be at the same potential (or have 0 volts between them).

in phase sine waves

So while this is not a multi phase system, it's also not a simple single phase system. Technically it's known as a "Single split phase system".

All of this; of course, assumes that the ungrounded (hot) conductors are from different legs of the service.