Inspector approved gas plumbing and followed up later, saying:
"Please note that we will be verifying the bonding of the new gas piping at the next inspection, please contact L&I for any questions regarding electrical. "

Gas plumbing will be connected to tankless water heater via flex hose. I'm assuming the flex hose doesn't count as proper bonding for the gas plumbing. So can I run a ground wire from the electrical outlet where the gas water heater will be plugged in or even bond to the water heater directly (since it is grounded via outlet plug)?

Best Answer

Grounding and bonding is a whole chapter in NEC. They're not all just the same thing.

Not least, every house has 2 different networks:

  • The Equipment Safety Ground which carries grounds from the service panel to all the appliances and outlets. This travels alongside the live conductors, as the green, yellow-green or bare wire in cables or conduits (or in the case of EMT, IMC or RMC, the conduit shell itself).
  • The Grounding Electrode System, which is the bond between the service panel and the actual earth: It is the heavy bare copper wire going from the service panel to ground rods, Ufer ground, or water main. (water main grounds are getting dicey because of smart meters).

The gas main should be bonded to the house's Grounding Electrode System.