Hello I was doing some remodeling in my kitchen and found a 2 pole 30amp 10-3 wire abandoned in a junction box under my kitchen island. its wired to my panel but the breaker was turned off and not labeled. I checked and it is live when the breaker is turned on. My question is can I branch out from this with smaller guage wire e.g. 12-2 or 12-3 for outlets and a sink with a disposal for my new kitchen island? I'm thinking no but not quite sure.
Electrical – branch off of a 2 pole 30 amp 10-3 wire found abandoned in a junction box
electrical
Related Topic
- Electrical – Wiring disposal/dishwasher/outlets in island
- Electrical – MWBC (Multi-Wire-Branched-Circuit) w/out joined breakers, how best to fix
- Electrical – How to add wiring to get the three-way switch to work properly
- Electrical – How to install standard outlets on a 30A #10 multi-wire branch circuit
- Electrical Issues – Why is 24 Volts in Kitchen Outlets Unless Two Breakers Are On?
- Electrical – Junction box with 12 and 14 guage wires
Best Answer
As long as the existing cable has a grounding conductor what you propose is absolutely fine, although you must replace the breaker with the proper two-pole 20A breaker. Although not required I would definitely place a label on the wire in the panel stating it is to be used for a 20A circuit maximum.