I have EMT leading to a metal junction box, and from that box goes plastic liquid tight to some equipment. Currently I have a ground conductor running all the way back to the panel, but I'm wondering if it's enough to terminate that ground at the metal junction box (so that the EMT back to the panel forms the remainder of the equipment ground).

Related question: how do I properly bond the 10 ga grounding conductor in the liquid tight to the metal box? Crimp a ring terminal on it?

Best Answer

Yes, it's allowable to tie a ground wire to a junction box and let the metal conduit carry it the rest of the way back.

However, if the ground wire is already in the pipe, I'd leave it in there - belt and suspenders - unless you need the conduit fill.

You terminate a ground wire at a junction box by attaching it to a ground screw. Virtually all junction boxes have a hole tapped #10-32 specifically for ground screws, which are sold either with or without pigtails. You can put 1 wire on that screw, or any sensible number of ring terminals. Make sure the ring terminals are UL listed for use in mains power.