So, let us assume we have a set of conductors (hot/neutral/ground) going off to some piece of utilization equipment. Can I also run a set of conductors of appropriate ampacity off this circuit to a subpanel, thus making the conductors both a branch circuit and a feeder at the same time, provided their ampacity isn't exceeded by the combined load? Or can a set of conductors be either a branch or a feeder under the NEC, but never both at once?

Best Answer

I'd like to see a real world example of this, but I don't think one could/would exist.

If you had a piece of equipment that required a 30 ampere circuit, for example. If you tapped a panel off that circuit, then you'd have to increase the size of the circuit, and/or follow the tap rules. The tap rules require overcurrent protection where the tap conductors terminate, so you'd need overcurrent protection at the new panel and the equipment.

So basically, the branch circuit conductors would become a feeder, and tap conductors would be used to tap the feeder.