Does the California Electrical Code allow one of the two required 20A circuits powering the wall / floor receptacles to also power a dishwasher?
Bonus question: If not, and the dishwasher requires its own circuit, may that circuit also power the gargabe disposal?
Please cite code sections if you can. My hunch is that the answer is 'no', based on this:
210.52 B.1
In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit,
the two or more 20-ampere small-appliance branch circuits
required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets
covered by 210.52(C), and receptacle outlets for refrigeration equipment.
and
210.52 B.2
No Other Outlets. The two or more small-appliance branch
circuits specified in 210.52(B)(1) shall have no other outlets.
Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electrical clock in any of
the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for
supplemental equipment and lighting on gas-fired ranges,
ovens, or counter-mounted cooking units.
thanks
tom
Best Answer
Update
Technically the two minimum kitchen, pantry, dining room, breakfast room, or similar area, small appliance branch circuit only applies to outlets served on the walls, counter-tops, and/or floor outlets if they are within 18" of a wall. All other appliances, with the exception of refrigerators, that are fastened in place, CANNOT be included on the two minimum small appliance circuits. They MUST be on their own appliance circuit.
Still though, you may be able to combine and share the dishwasher and disposal on one dedicated circuit if the following conditions are met.
References
NEC 2014