Can 2 romex cables be stripped before entering an EMT to allow more conductors in a 1/2" EMT? How would you transition from Romex to individual conductors going in or out of the EMT? Or is that allowed?
Electrical – Can the sheath of nonmetallic cable be removed prior to entering electrical metallic tubing (EMT)
conduitelectrical
Related Topic
- Electrical – Running NM-B in PVC SCH 40 Conduit from Outdoor Breaker Panel
- Electrical – Can non-metallic cable go up a wall shaft for a furnace vent
- Electrical – Will the last electrical receptacle on the same circuit have two cables entering the box
- Wiring – Installing vertical EMT conduit crossing a horizontal eletrical run
- Electrical – Sheath is too short! Can I finish in EMT
- Electrical – EMT to Top of Panel
- Wiring – Code compliance – how to pass EMT conduit through an interior wall
Best Answer
The wires inside Romex are THHN type, which is okay for EMT, but you cannot use a bare copper wire inside EMT. I would transition from Romex cable to EMT with a metal box. Bond the bare copper wires to the box with a grounding pigtail, and add a insulated green THHN wire to continue the ground through the EMT.