According to my understanding, if a supplementary ground rod is installed, it must be bonded to the existing rod via a buried 6 AWG cable (NFPA 70).
However, because virtually every side of my house is paved, I have no access to the soil around the ground rods. Could I use a 4- or 6-gauge wire running above ground through a PVC conduit via the basement to bond the two ground rods?
The new ground rod is for a TV antenna, and I have been told it is very unwise to ground it to the meter, which is just several feet away.
Note: The house needs to pass inspection, so please keep that in mind.
This question regards code compliance, which is not specifically requested in this post: Bonding Ground Rod for Rooftop Antenna.
Best Answer
I can find nowhere in the NEC that says that you must bury inter-electrode bonding jumpers. In fact, 250.64(B) explicitly allows for running grounding electrode conductors (such as inter-electrode bonding jumpers) along construction or otherwise aboveground when suitably protected against physical damage, etc.:
Of course, you'll have to double-check with your local inspectors, though -- they may have some local requirement for burial of bonding jumpers.