I am installing two wall ovens that each require 20 amp 240 volt outlets. I currently have wired for a single 40 amp 240 outlet. To convert without pulling new wire from the panel can I put in a sub panel an add two 20 amp 240 volt breakers that can feed the outlets I need? Is there any easier way?
Electrical – change a 240 volt 40 amp outlet for an oven to two 20amp 240 volt outlets
electricalwiring
Related Topic
- Electrical – add a 30 amp breaker to a sub panel being fed from a 50 amp breaker
- Electrical – have a 15 amp outlet on a 20 amp circuit with a 20 amp GFCI
- Wiring – run a 50 amp circuit for a hot tub from a 60 amp sub panel
- Wiring for new 40 amp wall oven and cooktop
- Electrical – Use a 50 amp / 240 volt outlet for car charger and snow melting system
- Wiring – How to intall GFCI breaker if wire for outlets is 12/3 using two breakers
- Electrical – changing 60 amp outlet to two 30 amp outlets
- Electrical – Two 240 volt runs off same breaker
Best Answer
Normally, you can never split a 40A supply to serve two loads rated for a 20A circuit. Except here.
This is an allowed exception for supplying oven/range loads. It's in NEC 220.55, referring to Table 220.55, Note 4:
NEC 220.55 and Table 220.55 also includes some derating (or more accurately, permissive up-rating) that overrides the normal "125% for continuous" derate found in NEC 210.19(A)(1). It appears to be permissive. Speaking of 210.19, ThreePhaseEel points out
This also overrides the 125% rating by saying a 40A breaker can definitely supply two 20A ovens, and saying a 8.75KW-9.6KW oven is allowed on a 40A circuit.