Electrical circuit

electrical

I have a storage shed that I'd like to run power to. My source is a former air conditioning circuit that I was told was 20 Amps, however when I took off the cover to the box out side, I saw 2 black wires and a ground wire. The breakers were removed due to the serviced being rerouted thru the main box near the meter. Can I still use this as the source if I reinstall a 20 amp breaker? And shouldn't it have a white wire?

Best Answer

The original circuit was a 240 volt circuit, so a grounded (neutral) was not required. Because of this, you only have two ungrounded (hot) conductors.

If these wires are part of a multi-conductor cable, and not individual conductors. The Authority Having Jurisdiction (AHJ) may allow you to reidentify one of the conductors, so that it can be used as a grounded (neutral). Check with your local building department, to determine if this is allowed.

Otherwise you'll have to pull a grounded (neutral), or new cable with a grounded (neutral) conductor.

You'll also want to check the gauge of the wires that are in place, as they're likely 10 AWG. While there's no problem using 10 AWG conductors on a 20 ampere circuit, you might find that the wires are too large to attach to devices (receptacles). If this is the case, you'll have to use smaller pigtails to connect the wire to devices. Check the markings on the device, to determine the acceptable wire gauge.