Electrical – Confused by ~115VAC 5-wire cabling to UK thermostat

240velectricalthermostat

I have a 5-wire cable as used for 3-phase (i.e. stripes/blue/brown/black/grey) coming to a hole where a thermostat was – only the earth, live (brown), and switched live (black) were used by this battery-powered thermostat.

Assuming that the 5-wire cable had been used simply to avail the black for use as a switched live, I thought that it would otherwise be like the 3-wire cables to a standard plug, and I could use it as such.

Confusingly, I measured 115VAC between live and neutral (expecting double, I'm in the UK). The same between live and earth; live and grey.

No matter, I thought, I can use a 100-240VAC -> 12VDC converter. Connected it, and then measured mere mV across its output. Strange – so I measured its input; found 7VAC. Repeatably.

I don't understand this – how or why is the voltage falling so drastically under (0.25mA) load, preventing the transformer functioning?

Do I have any alternatives? I don't understand why these lines are at 115VAC anyway.

Best Answer

Beware Ghost voltages

Typical UK central heating is wired like this (Honeywell Sundial S-Plan)

enter image description here

It is not immediately obvious but essentially, the 240 live supply passes through a series of switches in this order:

  • Mains supply (there is often a wall switch plate for heating). Provides power to ...
  • Timer (AKA controller - ST9400A/C in diagram). Provides power to ...
  • Room thermostat. Provides power to ...
  • Zone valve (when motorized valve is fully open it closes a switch). Provides power to ...
  • Pump and Boiler

Unlike the arrangements common in the US, all the above equipment operates at 240VAC.

Note that, so the switches in the timer and therostats don't have to switch the high currents needed by the pump, there is a separate (grey wires) parallel live feed to the mechanical relays in the zone valves. This doesn't change the fact that, logically, the units in the diagram operate in series.

Some commercial installations and some more recent domestic installations may have low-voltage to thermostats and may have intelligent thermostats that incorporate the timing functions. This doesn't seem to be the case in your installation.

As shown above, for installation convenience the equipment is wired radially and all connections are made in a central wiring box (often a backbox of the timer). So physically star-wired but logically in series (with parallel branches for hot water and heating).

Normally the thermostat needs 240 VAC neutral, 240VAC live (from timer) and switched 240V AC live (to zone valve). Some traditional-type thermostats include a heating anticipator (a resistor across switched-live & neutral that warms the thermostat).

UK wiring insulation colours are

            old           current

neutral     black         blue
live        red           brown
earth       green         yellow/green

Earth wires are sometimes bare copper (as in "twin & earth" single-core cabling inside walls/floor voids etc) but inside a junction box, back box or patress should be covered by the electrician in a yellow/green sleeve at time of installation.

If your thermostat has a ground connection but no neutral connection, it is wrongly wired and you should consult an electrician if you are not confident working with lethal voltages.

If the timer (controller) is set to "heating: always on" you should measure 220-240 volts on live at thermostat. Some multimeters have a low-impedance setting to avoid "ghost-voltage" indications. An alternative might be to temporarily wire a 60W incandescent light bulb across live and neutral, using a connector block, then measure voltage when the bulb is on (fully).