I have a Belkin Wemo switch that requires a neutral wire for installation. There is no neutral in the switch box. However, there is a neutral in the electrical outlet box below it, and a path from the switch to the outlet. Can I run a neutral wire from the switch to the neutral in the outlet box and connect it as a shared neutral? I guess this is another way of asking of all neutral wires are basically interconnected eventually (leading back to the main electrical box) and whether any neutral in the house can be used by anything requiring a neutral.
Electrical – connect to any neutral wire in the house
electricalwiring
Related Topic
- Electrical – What are the risks of sending low-current neutral through the ground wire
- Electrical – Can ground shock me? It’s bonded to neutral in the panel
- Electrical – How to connect a neutral wire to a bundle
- Wiring – How to be sure a wire is truly neutral
- Electrical – Can two neutrals on different legs of the same circuit be connected together to shared neutral of ceiling fan
- Electrical – use this neutral wire running through the switch box for the smart switch
- Electrical – connect the neutral wire ends via a single switch terminal (without a pigtail)
Best Answer
According to 2011 National Electrical Code article 300.3(B), No. For verbiage, see this answer. For one explanation why, see this answer.
Another reason not to do it, is because you could end up overloading the grounded (neutral) conductor. Depending on if the two circuits are on the same branch circuit, different branch circuits on the same leg, or different branch circuits on different legs, you'll run into different situations. However, in two out of three of these situations, it is very easy to overload the grounded (neutral) conductor.
Examples:
Let's examine what happens in a 120/240V single split-phase system, in a few different configurations. The circuit breakers in these examples is a combination circuit breaker, with 15 ampere thermal overcurrent protection and magnetic short-circuit protection.
Load on a circuit
With a single branch circuit supplying a 15 ampere load, we see that there will be 15 amperes on the grounded (neutral) conductor. This is fine, since the grounded (neutral), and ungrounded (hot) conductors are both sized to carry 15 amperes.
Two loads on the same branch circuit
In this situation, we'll see 30 amperes on the grounded (neutral). However, since we're also drawing 30 amperes through a single breaker with 15 ampere overcurrent protection, the breaker will open.
Two loads on the same leg, but different breakers
This is the dangerous situation, since the breakers will not trip. Each circuit will draw 15 amperes on the ungrounded (hot) conductor, but the grounded (neutral) conductor will see 30 amperes. Since the conductor is only rated for 15 amperes, the conductor is in danger of overheating and starting a fire.
Two loads on different legs
If the two loads are on different legs. You'll find that while each ungrounded (hot) conductor sees 15 amperes, the grounded (neutral) carries 0 amperes.