Electrical – Connecting 240 volt generator to Main Panel

240velectrical-panelgeneratortransfer-switch

I read previous posts that explained that the Sub Panel has a separate connection for ground and separate for neutral, while the Main Panel does not separate the ground & neutral – this is exactly how my panels are setup. My Sub Panel has all of the house's breakers and the panel is completely full. My Main Panel has the one Main Cut Off with areas to add breakers. I'm wanting to add a double breaker to the Main Panel for a 240 volt generator.

I have two questions:

  1. When I wire the generator inlet to the Main Panel, do I wire both the ground wire and neutral wire to the same connector as is done now with the ground & neutral at the Main Panel?
  2. The generator's owner's manual states that it's "neutral floating". I was intending to ground the generator (8' copper rod with 6 ga. solid copper). Does the floating neutral on the generator change anything?

Best Answer

The floating neutral is good news, but you don't need a ground rod for this

The fact that your generator has a floating neutral is actually quite fortunate for you, as breaker-interlock-based transfer setups are largely incompatible with generators that have bonded neutrals (the more common case). However, since you're plugging your generator into your house, which already has a grounding electrode system (ground rods, etc), you don't need to add a ground rod at the generator, as the house supplies both the grounding electrodes and the neutral-to-ground bond point.

As to the inlet, since it's your main panel, you can land both wires on the same bar

A common "shortcut" in main panels (esp. in residential work) is to slobber all the neutrals and grounds onto the same bar, since that's where neutral and ground meet. Since most panels where this is done don't have separate ground bars fitted to begin with, you're left with little choice but to continue this practice, unless you wish to buy a ground bar kit for your specific make and model of panel and add a separate ground bar.