Electrical – Connecting the four terminals of a 14-50P to a homebrew 240v system with three wires

240velectrical

I bought a new 240v homebrew system. The system requires a 30 amp circuit and comes with 10 gauge wires (black, white, green) but no plug (so you can connect the plug needed for your situation).

I also recently bought an electric vehicle so I had a 14-50R installed in my garage with a 50 amp GFCI breaker.

I want to connect my system to the 14-50R, so I bought a 14-50P to connect to the bare wires from the system. The issue I have is that the 14-50P has 4 terminals (2 hot, 1 neutral and 1 ground), but there are only three 10 gauge wires coming out of my 240v system (1 hot, 1 neutral and 1 ground). The terminals in my 14-50P are removable, so should I connect the 1 hot, ground and neutral and remove the unused hot terminal? Or should I do something totally different? And am I okay using the 10 gauge wire since the system will only draw less than 30 amps?

Best Answer

If it's 240 volt it doesn't have a neutral. So your home brew has 2 hots and a ground.

Just wire it with the reverse pattern of the receptacle except for the neutral (white) wire will be deleted from the plug.

10 gauge is good for 30 amps but understand the receptacle is protected with a 50 amp breaker so if your homebrew has a recommended max size breaker less than that you will be exceeding the recommended protection for your brewer.