Is it OK to have a consumer unit in a downstairs cloakroom off the main entry?
The unit is between basin and toilet, at head level, 50-100cm horizontal distance from the basin. This is how the house was built in 2003.

I am having some changes done, including a consumer unit with more switches, and the electrician says the consumer unit must be moved out, for instance into the entry.

It is obviously not the ideal place, but must have been approved originally. What do the regulations say?

Best Answer

What do the regulations say?

The law says remarkably little.

You can download Approved Document P: electrical safety, dwellings

It says things like

P1. Reasonable provision shall be made in the design and installation of electrical installations in order to protect persons operating, maintaining or altering the installations from fire or injury.

and

Additions and alterations to existing electrical installations

1.6 Regulation 4(3) states that when building work is complete, the building should be no more unsatisfactory in terms of complying with the applicable parts of Schedule 1 to the Building Regulations than before the building work was started. Therefore, when extending or altering an electrical installation, only the new work must meet current standards. There is no obligation to upgrade the existing installation unless either of the following applies.

a. The new work adversely affects the safety of the existing installation.

b. The state of the existing installation is such that the new work cannot be operated safely

(my emphasis)

and

Electrical installations should be designed and installed in accordance with BS 7671:2008 incorporating Amendment No 1:2011

Note that "should" is not "must". In practice, a DIYer or self-employed electrician would not have the resources to use another standard.

BS 7671 is a publication of the IET & BSI and can be purchased from the BSI for £85.

I'm not an electrician so I haven't purchased a copy, I'm reasonably sure that it permits consumer units in rooms containing a toilet and washbasin. BS 7671 is stricter about what goes in rooms containing a bath or shower.

The builder probably located it there because it was convenient (probably utility owned meter on other side of wall) and cheaper than putting it somewhere more sensible.

Note that the IET say

No, when installing a new circuit to an existing installation, after 1st January 2016, providing there is a spare way on the existing consumer unit, or if you utilise an existing way, there is no requirement to upgrade the consumer unit from a plastic product to a new metal type.

So adding new circuits is not sufficient justification by itself for relocating a consumer unit.