I'm installing a 200 amp automatic transfer switch but my main service entrance is a combo meter box that breaks out into two 100 amp since there are two subpanels downstream. I'm thinking of combining the hots from both of these breakers using a couple of Morris Products 97643 Multi-Cable Connectors to feed the ATS.

After the ATS I will go back to a dual 100 amp panel to feed the existing subpanels. I'm wondering if there is a better way other than upgrading the combo meter box?

Here is an image of the main combo panel:

Best Answer

No, you definitely can't do that with this meter-main! You have several choices.

Put only one panel on the ATS

This is the normal approach to this problem. You pick one panel and make it the ATS-operated panel. Any critical loads in the other panel, you reroute them.

You can also put the other panel on a MTS (manually operated interlock) and those are $100-ish for most panels.

Two ATS's, one for each panel

This is also allowed though at higher cost and complexity, of course.

An ATS that stacks under the electric meter.

Some ATS's have a funny plate that fits between the meter pan and the meter, thus switching the entire service. That type of ATS will work very well in this instance.

Replace the meter-main with something appropriate

Into the trash goes both the meter and the dual main breaker apparatus. Then you fit a meter-main designed to support an ATS, or a plain meter feeding the ATS which then feeds a 200A panel which has the two 100A breakers in it.