I have installed a 75 amp sub panel with three #6THHN and a #8 ground from the main.
I need to move two branch circuits from main to sub since I do not have space in the 200amp main for the sub panel breaker.
Is a ground wire required for each branch circuit if they are in the same conduit as the feeders for the sub? One inspector said that each circuit has to have a ground. It seems redundant.
Best Answer
No, one ground wire of sufficient size will do the trick
All the branch circuits in a single cable or conduit can share a single ground wire (and are often forced to when metal conduit is used as a ground path or when a multi-circuit cable is used). This is permitted as a consequence of NEC 250.122(C):