Ungrounded "hot" conductors can be identified by any means that is not used to identify grounded "neutral", or grounding conductors. So basically if it's not white, gray, any color other than green with three continuous white or gray stripes, green, green with yellow stripes, bare, or any of the other identification methods below, it can be an ungrounded "hot" conductor.
Blue is an acceptable color for the insulation on an ungrounded "hot" conductor.
National Electrical Code 2014
Chapter 2 Wiring and Protection
Article 200 Use and Identification of Grounded Conductors
200.6 Means of Identifying Grounded Conductors.
(A) Sizes 6 AWG or Smaller. An insulated grounded conductor
of 6 AWG or smaller shall be identified by one of the following means:
(1) A continuous white outer finish.
(2) A continuous gray outer finish.
(3) Three continuous white or gray stripes along the conductor's entire length on other than green insulation.
(4) Wires that have their outer covering finished to show a white or gray color but have colored tracer threads in the braid identifying the source of manufacture shall be considered as meeting the provisions of this section.
(5) The grounded conductor of a mineral-insulated, metal-sheathed
cable shall be identified at the time of installation
by distinctive marking at its terminations.
(6) A single-conductor, sunlight-resistant, outdoor-rated
cable used as a grounded conductor in photovoltaic
power systems as permitted by 690.31 shall be identified
at the time of installation by distinctive white
marking at all terminations.
(7) Fixture wire shall comply with the requirements for
grounded conductor identification as specified in 402.8.
(8) For aerial cable, the identification shall be as above, or
by means of a ridge located on the exterior of the cable
so as to identify it.
Article 250 Grounding and Bonding
250.119 Identification of Equipment Grounding Conductors. Unless required elsewhere in this Code, equipment grounding conductors shall be permitted to be bare, covered, or insulated. Individually covered or insulated equipment grounding conductors shall have a continuous outer finish that is either green or green with one or more yellow stripes except as permitted in this section. Conductors with insulation or individual covering that is green, green with one or more yellow stripes, or otherwise identified as permitted by this section shall not be used for ungrounded or grounded circuit conductors.
Best Answer
Short answer: No
The National Electrical Code contains no particular color code for phase conductors. Brown is an acceptable color for the ungrounded conductor.
Green with a yellow stripe is used in a lot of equipment imported from Europe and is also acceptable to the NEC
The blue neutral is also not a problem.
So, you could argue the fixtures are not appliances and therefore the neutral cannot be light blue but the last line says you can re-identify the light blue to white or gray.
So, it appears you can use the cords either way.
Happy day!