I am planning to pull three sets of four conductors (3 AWG wire) through 2" EMT conduit for a 30' length that is common to all three sets of wires, and then branch off at a listed metal junction box (10"x10"x4") to three 1 1/4" EMT conduits. I am doing this because I am planning to run wiring for three 100-amp subpanels from a 200-amp main.

I was not planning to make any mechanical connections inside of the junction box and just use the junction box to pull the wire through. Do I have to strip back insulation on the ground wires to make direct connections to the junction box?

Best Answer

250.4(A)(2),(3), & (4) says that "Normally noncurrent-carrying conductive materials enclosing electrical conductors or equipment" should be grounded and bonded. So while you may not have to connect the equipment grounding conductor to the box, the boxes do have to be grounded and bonded. Since you're using EMT, the boxes can be grounded and bonded via the conduit. If you were using nonmetallic conduit, you'd have to ground the boxes some how.