Is there something on the NEC code that states the UFER ground needs to be permanently visible? I had my rough in electrical inspection the other day. He stated that per NEC 250.64(E) (1), I have to put an access panel in the drywall so that he is able to visibly see the UFER. I would rather not have an extra hole in my finished ceiling if not needed. Nothing I find is saying this is needed.
Electrical Grounding – Does the UFER Ground Need to Be Visible?
drywallelectricalfoundationgrounding
Related Topic
- Drywall – Paint Peeling, maybe gypsum paper too
- Electrical – Only 1/8″ of NM cable sheathing in electrical box
- Electrical – Does the NEC define a “dining room”? 210.52(B)(1)
- Electrical – Does 5V DC power supply require Ground wire
- Drywall – Cutting and repairing drywall ceiling above shower stall
- PVC Conduit – Using Schedule 40 PVC to Protect a Grounding Electrode Conductor
- Horizontal Crack in Foundation
- Electrical – Refrigerator on a shared electric line with Stove and 5 countertop outlets
Best Answer
Wrong citation, right answer
Your inspector is right, even though their NEC citation isn't. They're after NEC 250.68(A):
So, you'll need to provide that access hatch for the "stub-up" connection from the rebar to the grounding electrode conductor, or provide some other way to access it. If the connection is irreversable, using exothermic welding or a listed compression connector, instead of being a mechanical clamp, though, then you can cover it over -- this might be worth discussing with your electrician.