Electrical – electrically isolate appliances by putting them on separate legs of a split phase supply

electricalload

In my office, I have a server (powered through a UPS) and a laser printer on the same circuit. When the laser printer turns on, the lights dim and the UPS will briefly switch to battery. This prematurely wears out the battery, and, if there were no UPS, would cause extra wear and tear on the server's power supply.

Can I electrically isolate these two from each other by putting them on separate legs of my house's split-phase power supply? In other words, do loads on one leg of a split-phase power supply affect loads on the other leg?

Possibly related answer here.

Best Answer

If the outlets are on completely separate wire runs from the breaker panel OR sharing a neutral but on opposite legs (sharing on the same leg is illegal), then the wire resistance from the panel to the outlets will be isolated between them and the voltage drop will be minimized. (The current draw is low enough that there should be no noticeable drop at the panel).

So yes, even if they were on the same breaker, let alone phase, as long as the wire runs are separate, the server should not see a drop from the laser printer. Also good if a neutral is legally shared.

(The reason that the shared neutral is OK is that each circuit's return current will be 180 degrees out of phase. Therefore, the worst case current through the neutral will be one circuit's. In fact, when the laser turns on, the voltage may even rise slightly to the server as some of the server return current will actually flow through the laser, bypassing the neutral.)