Electrical – EMT or PVC Conduit For Exterior Above Ground Electrical Run

conduitelectricalgarage

I'm installing a garage on the side of my house furthest from the electrical box. I don't want to trench the entire distance (60 ft), so I am planning on running conduit along the exterior of my home to the wall nearest the garage. From there I would dig my trench to run to the garage (~ 10 ft), and transition from an above ground to a below ground installation. I'm planning on a 60 Amp circuit to power the garage. EMT can be placed underground according to 358.10.A.1. If I read correctly it only needs to be buried 6 inches, where I need to go 18 with PVC. Am I understanding this correctly or off base in my analysis? What would be the recommended choice in this instance.

Best Answer

If you do use EMT outside or in ground you will need to use compression couplings listed for wet/ damp locations, it will need to be secured every 10' and within 3' of the boxes. EMT would require 18" burial depth. Knowing you are going from 1 end of the home down then back up you will have more than 360 degrees of bends so conduit bodies or boxes will be needed to provide pull points. I will usually use conduit bodies to go around corners makes a tight turn with a LB then further away I will use another to make the turn to go in the ground LR or LL with 90 deg sweeps in the bottom of the trench at both ends and a LB or box to enter the building (box being a exterior disconnect). I think you might find schedule 80 PVC a bit cheaper and easier to work with than 1" or greater EMT.