I will be installing a 230v 20a outlet. To run the cable, it will run down the wall of my living room (brick house). The cable will be 10/3 cable (the orange plastic wrapping). What is the proper way to protect the cable? Will the stick-on cable management system be enough, or do I need conduit?
Electrical – Enclosing cable run through living space
electricalwiring
Related Topic
- Electrical – Can i run the cables from the outside box to the inside breaker box through 2×4 studs
- Wiring – How to run Ethernet cable along a brick wall
- Electrical – run two cables through the same conduit
- Electrical – What type of cable should I run to future-proof an outlet for an air conditioner
- Electrical – Short conduit run from attic to exterior panel. What is the correct way to run cable
- Electrical – remove the sheathing from cable just where it passes through conduit
- Electrical – wire a 120v 20A outlet with #8 wire
Best Answer
You can't use cable management systems. They are not listed for protecting mains wiring. At best they're listed for extension cords, but probably not.
You can use UL-listed surface conduit such as Legrand Wiremold. You can also use regular conduit if you don't mind the industrial look and chicken-choking the cable down the conduit. I recommend EMT because it's not bad to work with, and is easy to correct or modify.
Either way, you can use the conduit in one of two modes:
For a 20A receptacle and breaker, you are perfectly allowed to use 10 AWG wire. However, you don't need to... you can do it with #12 wire. At 230V, #10 is best if you are going over 150 feet.
Also, for an air conditioner (NEMA 6-20 outlet), you don't need a neutral wire. However, including a neutral wire will allow you to convert it to two 120V circuits later. If you wind up doing the entire run in actual conduit (EMT or Wiremold), you can run individual wires, omit the neutral wire for now, and add it in the future when you need it.
If you use metal non-flexible conduit, that is a valid grounding path (indoors), which means you don't need to run a ground wire. My air conditioning circuit is simply 1/2" EMT conduit with a black and red THWN-2 wire inside. That is it.
* I'm assuming you are using round 10/3 cable. If you're using flat cable, measure its widest dimension. multiply by 1.37, and you need to use conduit whose inside dimension is larger than that.