Your electrician could add a SquareD sub panel that would have the four SquareD AFCI breakers, fed from the GE panel with a standard two pole breaker.
AFCI breakers can be sensitive to certain loads. I've experienced problems with florescent lighting, power tools, and vacuum cleaners tripping the breaker.
Some surge protectors work by "redirecting" surges to the equipment ground, which is pretty much the definition of a ground fault. In this case, it's definitely possible that surge suppressors could be tripping GFCI receptacles/breakers (given a large enough surge).
As for the AFCIs... When electrical contacts separate, they often create an arc between the contacts. This arc spans the gap until the contacts are too far apart, and the arc can no longer be sustained. It's possible (in theory) that the GFCI tripping could create a large enough arc, for long enough to cause the AFCI to trip. It's not likely that a properly functioning GFCI would do this, but if the GFCI was old and worn it could be opening the contacts slow enough that a detectable arc is being produced.
Determining if the GFCI tripping is causing the AFCI to trip, is a simple test. Simply press the test button on the GFCI. If the AFCI trips, you'll have figured out half the problem. If the ACFI does not trip, you could repeat the test using a receptacle tester with a GFCI test function.
![enter image description here](https://i.stack.imgur.com/RCjG1m.jpg)
If it's determined that the GFCI is causing the AFCI breaker to trip, replacing the GFCI receptacle may resolve that part of the issue.
Figuring out if the surge suppressor is tripping the GFCI, is a more difficult proposition. It will likely require you to monitor the supply voltage over some time, to identify and document possible surges.
Best Answer
If it's officially considered "habitable space", then it's a finished basement and GFCI is not required.
AFCI protection is required. An AFCI breaker, is probably the cheapest and easiest way to provide the protection.