The two copper wires inside our furnace, that are supposed to ignite the gas, get too dirty to do the job about twice a year… We then have to go there — always at inopportune times — remove two screws, pull the thing out and apply sandpaper.

Can anything be done to solve this problem once and for good (or, at least, for some years)?

Should I, for example, try to gold-plate the copper after cleaning it again with something like this? Or will the deposits simply settle on the gold just as they currently settle on the copper?

The device is a Peerless PureFire, about 9 years old. This is a "high efficiency" unit — there is no "pilot light". Instead, the fuel (natural gas) is ignited by electrical spark.

Best Answer

There are other types of igniters but a plating will not help. Contaminants build up on the electrodes and this reduces the ability to create the spark. Dust and smoke in the air are the big sources. Since you know it needs to be maintained 2x per year the best option is to preform “preventive maintenance” clean the contacts prior to the heating season and maybe 1/2 way through. If the electrodes are cleaned when the time is better for you it would not happen when you need heat. 2x a year is more often than I have normally experienced, you may need a service on your burner to make sure it is burning clean and not part of the problem, electrostatic air filters also help to filter out things that can pass through most furnace filters but these need regular cleaning also (some monthly during heating / cooling seasons).