Electrical – Garage upgrade from 20 AMP to 50 AMP

electricalelectrical-panelgaragesubpanelwiring

I bought a house recently and I have some experience with electrical but I am not fully sure what would be the best course of action since I've never had a detached garage where the cable would be buried between the house and the garage.

I already have a 20 amp breaker in the main panel and a subpanel with 2 breakers at 15 amps in the garage. They are currently wired with a 12/3 gauge cable.

I would like to upgrade to a 50A breaker on the main panel so that I could have in the garage sub-panel:

  • 20A 120v breaker
  • 20A 240v breaker
  • 15A 120v breaker

Would you all be able to help me try to figure out what I should do?

My current plan was to buy about 100 feet of 6/3 Romex and use the currently buried conduit to pass the new wire and install on the current main panel a 50A breaker.

My main panel is 200A, currently in NJ in case anyone knows any code problems that I should be aware of.

Where the conduit leaves the house:

Best Answer

"Romex" (brand name) is usually used to refer to NM/B cable, which cannot be run in conduit that runs outdoors. It its not rated for wet locations, and all exterior conduits are wet by definition and in reality.

It's also a huge pain and requires huge conduit to run the UF cable (similar to NM/B, but waterproof, with a gray jacket, typically) in conduit.

Use THWN wires in conduit. If you don't want to run conduit the whole way, use a junction box at the end of the conduit to transition from wires in conduit to cable not in conduit.

Edit: if you want 50A service to the garage, you'll need to dig a new trench for new, larger conduit to the garage, since your conduit is 1/2" PVC. Be aware that your conduit MAY not actually extend the whole way - you may just have two shrt sections where the present cable goes into and comes up from the ground, with the UF cable "direct buried" with no conduit in between. That is a legitimate install method with UF cable (the conduit is "protection from physical damage" at the ends where it comes up) but less desirable (no ability to remove and replace the wire without digging it up - also less protection in the ground than wire in conduit.)